Hi guys , what different ways do you all test for insulation / resistance test ??
The way of testing with 500v with removal of all lamps , appliances etc is a bit demanding at times .
Any thoughts ??
On a PIR that maybe the only way you can test L-N connected then to earth. If you have a factory with hi bay lighting are you going to start to disconnected each luminaire ?
Also have a read of regulation 612.3.2
Agree that an initial verification should be done at 500v between all conductors and it is poor planing not to do so, but sometimes on a PIR you don't have many options
Reply to insulation / resistance test in the Australia area at ElectriciansForums.net
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...