Anyone who knows. Lighting circuit with MAINS voltage LED downlighters. If I do a 500v Insulation Resistance test on LED bulbs. Will it knock out the bulbs.
I know its electronic equipment that gets destroyed predominently.
Its quite a few down lighters, didn't want to hit the button without checking. Costly mistake.
 
Never tried it and never will. Pound to a pinch of poo it will fry the LED's, or they'll glow very brightly.
 
Anyone who knows. Lighting circuit with MAINS voltage LED downlighters. If I do a 500v Insulation Resistance test on LED bulbs. Will it knock out the bulbs.
I know its electronic equipment that gets destroyed predominently.
Its quite a few down lighters, didn't want to hit the button without checking. Costly mistake.

When you're doing a (Periodic) inspection, all you need to do is IR between L&N to Earth.
If in doubt, start with 250V.
 
Hi Ebow,

Thanks for your advice. Think that might well be the safe option on this circuit.

first lighting circuit install as part of dare I say it PART P. Doing the testing ready for building control electrical testers to check my work before I can join a registering body.
Plumber by trade. Did the Part P so I can use it during the course of my work. I know fully qualified proper electritions dont like this much but it assists me to be more versatile in these difficult times.

Ian
 
I'd never take the risk, as previously posted L&N - E will be sufficient, or limitation on periodic. I'm assuming it's not an install cert for obvious reasons.
 
Hi Ebow,

Thanks for your advice. Think that might well be the safe option on this circuit.

first lighting circuit install as part of dare I say it PART P. Doing the testing ready for building control electrical testers to check my work before I can join a registering body.
Plumber by trade. Did the Part P so I can use it during the course of my work. I know fully qualified proper electritions dont like this much but it assists me to be more versatile in these difficult times.

Ian

I am sorry but others may have missed this post. If this is a new install then all the dead tests should be performed before any circuit is energised, all the lamps should be removed and the insulation tests carried out properly. The correct procedure would be to test each cable against each other freely, then connect the earth to the MET and test against earth, this will establish any faults in the cable during installation.
If it is a periodic then the described methods above will suffice, never test at full d.c. voltage until you are sure. It saves you some embarrassment.
 

Reply to Insulation resistance test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
312
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
941

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
483
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top