Guest 004

This is proving to be a pain in the backside. It just impractical to disconnect the emergency, as they are hard wired. So apart from putting notes on the test sheets, how can I get good readings, at present I am getting 100 ohms on all conductors, with emergency connected. When the emergency's were removed from the circuitry, readings were greater than 200 megs.

Any advise would be greatly appreciated.

IQ where are you:)
 
Reg 612.3.3 just do the test between lives connected together and the CPC. I know it is an initial verification as such, but your just the tester, and so I assume that is the only part of the EIC you will sign.

I would do it at 250v first and as it is an initial verification if you got good results do another at 500v. The 500v between LIVES-EARTHS should not cause you any problems.
 
Hi MrEnigma, I will do the same as Malcolmsanford suggested by putting the neutral and live wires together and test them against earth with the lamps in, first at 250v and then at 500v. I think you will get the right readings by this method. Hope this helps
 

Reply to Insulation Resistance testing of Emergency Lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top