Insulation Resistance testing procedure | on ElectriciansForums

Discuss Insulation Resistance testing procedure in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

DaveS

-
Joined
Apr 30, 2014
Messages
76
Reaction score
14
Location
London
Hi all

Am doing 2394/95 at moment and trying to get procedure firmly stuck in head. Thing I'm getting a little bit confused with is with some of the vids/examples online some state to switch main switch on (obviously before supply connected) and others off. My thinking is that you might as well always leave off as you will only be testing from the load side terminal of this switch anyway? What would be the other reason for leaving on. The other thing not to sure about is why the need to link N and L terminals at board in some instances doesn't just testing outgoing live and earth bar give a complete reading. Sorry if missing something really obviously long day!
 
1.you r IR tests should always be done with the main switch locked off and the installation isolated.
2. you link L-N in the DB and test from LN - E if you have any equipment on the installation that may be damaged by the test. e.g. any IT gear, boiler PCBs, TVs etc.
 
Cheers lads just think I'm nit picking a bit really. Had checked them vids just think I need to watch how question worded and make sure I explain clearly also clarify when testing thru sensitive equipment and linking out
 
Just think in a logical manner, you'll get it ingrained in no time.

also remember: check where conductors go, before sending 500v through them - I've seen this done a few times now.
 

Reply to Insulation Resistance testing procedure in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top