Lads,
I am soon to be doing an EICR on a large working mens club (not being paid in ale). My question is this...There is going to be lots of lamps i cant take out,equiptment still plugged in that i cant find etc etc so im gonna have to test between L-N to E .
When carrying out the IR test at the sub boards i want to try and test the whole board in 1 go. My way of doing this would be to isoloate the supply to the sub board im testing,disconnect the supply cable, then link out the main switch with a piece of 16mm2 cable and test to earth. Is this the way you boys would do it?. I know if i get a poor reading i will have to test each circuit on its own.
Any thoughts would be tremendous.
I am soon to be doing an EICR on a large working mens club (not being paid in ale). My question is this...There is going to be lots of lamps i cant take out,equiptment still plugged in that i cant find etc etc so im gonna have to test between L-N to E .
When carrying out the IR test at the sub boards i want to try and test the whole board in 1 go. My way of doing this would be to isoloate the supply to the sub board im testing,disconnect the supply cable, then link out the main switch with a piece of 16mm2 cable and test to earth. Is this the way you boys would do it?. I know if i get a poor reading i will have to test each circuit on its own.