Depends if there is a need to test L-N. If you are testing new work then a full test between live conductors and lives to earth should be carried out. If it's an EICR or a test on an existing circuit where you are not entirely sure of the layout then a LN-E test is the only practical way, in which case there is no reason to disconnect loads. Try disconnecting 20 downlights before carrying out a L-N test......I don't think so.
 
If you are testing new work then a full test between live conductors and lives to earth should be carried out.
Depends. Many countries only require a Live/Earth insulation test rather than a Live/Live one. Generally it's the insulation resistance to Earth which we are trying to ascertain for the installation, although obviously in some places it's between all conductors.
 
If you need to test between line and neutral then yes connected loads need removing/isolating. If you are carrying out some kind of periodic inspection then generally a line to neutral test isn't really necessary.
 

Reply to Insulation Resistance Testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
286
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top