Hi guys, I obviously know how to conduct a IR test but I'm just looking for a few tips, I was doing a lighting d\b today and obviously I never did a L-N test as it was a massive building and not feasible to disconnect all lamps. It was a triple pole +N mainswitch so I isolated the board, it is just a report I was doing so no need to get deep into the problem, I started by testing between live to earth and considering it was a 12-way board (36 circuits) only 15 circuits were clear and the rest were either a dead short or around the 0.5M ohms .
1 . Is it more than likely a neutral to earth fault ( voltage up line through lamp and back down neutral ) rather than L to E as a L to E would trip the mcb.
2. Does a lamp effect L to E or N to E readings
3. If there is a fault to neutral on a lighting circuit does this have an effect on all circuits until this neutral can be traced and disconnected from neutral bar ( e.g if I find a problem with 1 circuit will it clear the other16)
4. I'm only new to testing so any advice and routine for finding a fault doing a IR test would be gratefully appreciated
THANKS GUYS