So i have db1 in 1 block of flats for communial lights etc, feeding db2 via a swa feed underground. Ir at db1 to test every circuit and submains 0.01Mohms. (N+L together to earth)
Switch db2 off. All clear. Db2 also all clear when testing ir when investigating further.
Any suggestions??
 
From what you describe, everything correctly wired and DB1 and DB2 with DB2 on are 0.01MΩ and with DB2 off is >200MΩ and all of DB2 is >200MΩ there can only be fault within the main switch of DB 2 to earth!

Since this is not possible unless there is a huge metal spike through the switch there is something missing. Did you test DB1 and DB2 together after testing DB2 as clear as it may have then been OK.
Perhaps someone realised you were testing and removed the offending item.
(I have had this; testing a circuit found the fault left one faulty cable, one OK cable sticking out went to get a new cable, test again and both cables are now at fault, the customer had been "helping" by plugging everything back in, as I was nearly finished!)
 
From what you describe, everything correctly wired and DB1 and DB2 with DB2 on are 0.01MΩ and with DB2 off is >200MΩ and all of DB2 is >200MΩ there can only be fault within the main switch of DB 2 to earth!

Since this is not possible unless there is a huge metal spike through the switch there is something missing. Did you test DB1 and DB2 together after testing DB2 as clear as it may have then been OK.
Perhaps someone realised you were testing and removed the offending item.
(I have had this; testing a circuit found the fault left one faulty cable, one OK cable sticking out went to get a new cable, test again and both cables are now at fault, the customer had been "helping" by plugging everything back in, as I was nearly finished!)

Im certain nobody touched anything being as it was the communial installation. Very strange though. But a ir test at db2 to prove no faults didnt really require another test back ad db1 being as all was clear.
 

Reply to Insulation Resistance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
1K
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
Replies
24
Views
3K
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
975
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
377
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
818

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks