Evening all,

Been to a job today to add some sockets to a ring, Did a quick IR test and got >299 L-N >299 L-E & 35 N-E, checked out continuity, Zs, all fine, the L-E has got me a bit stumped, any ideas? cheers.
 
Evening all,

Been to a job today to add some sockets to a ring, Did a quick IR test and got >299 L-N >299 L-E & 35 N-E, checked out continuity, Zs, all fine, the L-E has got me a bit stumped, any ideas? cheers.

Cable been damaged somewhere, either something has partially breached the sheath or its squashed somewhere,or in a socket or switch box, can you break the circuit down into legs to find out which leg is at fault?
 
Also you did isolate the neutral and earth at the board didn't you? ;)
Don't forget resistances in parallel like that will be reduced.
Other than that ^^^^what he said, take a socket off and test either way, keep sub-dividing. Good luck.
 
Thanks guys, I am not planning to investigate further it is well in spec, it was just the difference that had me thinking, somtimes thinking too much!
 
why does this need investigating 35 meg is well in

While this is true, I would always mark down on the Minor Works Cert as a footnote to have a Periodic carried out within a year. That way youve sort of covered your behind.

It is important to have the Periodic carried from time to time because that 35 meg is probably going to get less and less until the lights go out. By keeping an eye on the numbers dropping over a period of time you can then decide when enough is enough and further investigation should happen.
 

Reply to Insulation Resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
763
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
765

Similar threads

The instructions tell you to test the insulation and you already know from the result of the previous test that the L and N are not insulated from...
Replies
4
Views
527
davesparks
D
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
479

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top