Insulation resistance | on ElectriciansForums
Discuss Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
C
Cj24
Hi can you please tell me in idiot form how is best to do a insulation resistance test and what results I should expect thanx
The best thing you can do is get a lenght of cable of your own and then at 500v setting
test live to neutral
test live to cpc
test neutral to cpc
Then if you have any neons or sensitve equipment that cannot be disconnected from the circuit clip live and neutral together on one clip earth to the other clip and test that way it wont damage anything.
The test on your cable with give you the results you want from real tests.
Chris
Reply to Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
M
Heat resistant paste?? Hi guys What do you guys use when having to solder close to plastics? Are the pastes any good or not? If so, what products...
macka09
M
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.