Im with rocker on this one doesnt take much more time to megger each circuit individually on the dead testing procedure before reconnecting .

The problem is it doesn't address what the test is designed to confirm, which is the cumulative effect.

1/Rt = 1/R1 + 1/R2 +1/R3 etc.

Rt = 1/(1/R1 + 1/R2 + 1/R3 etc.)
 
Here is a extract from Guidance Note 3 if that helps.

2.7.7 Insulation Resistance:
"Simple installations that contain no distribution circuits should be tested as a whole"
 
149 Mohms is still a very high reading and nothing to be concerned about, a lot of people when just starting out testing make the same mistake and expect to see a reading of >299 every time

readings will always vary and depending on age of installation etc will depend on how you react to it,

for example an old instalation showing 20- 30 Mohms would be recorded but not concerned about, however if this was a new build or rewire etc then id be wondering why the values are low


Agreed. did an insul resistance test on a new install and got a 40M ohm on the downstairs ring main. Investigated and found rodents had munched their way though the cable. Told the customer his new wiring needed to be replaced and the rodents 'evicted'.
 
And if we aren't testing the full installation, for a minor works cert for example? It would be unreasonable to power down a whole house for the sake of changing a lighting pendant, but if we measure at the bars for L2 and LN with a live installation then we are going to get inaccurate readings, no? Also. if we are supposed to be testing the whole installation, then once again again when we are changing that lighting pendant we will be siging our names to a cert that says the whole installation is safe.

If I'm testing the whole installation, I will do each circ seperately, then test bar to bar CPC to neutral, and test from bars to lines on each circ to test for faults between different circs, but on most minor jobs, I wouldn't.
 
Last edited by a moderator:
Yea, that's what I'm saying. But if, as is being suggested here, we should not be testing individual circuits and should be testing at the bars, then doing this will mean that we are testing every other circuit, and not the one we have worked on. If I am testing an individual circuit, I:
open breaker
D/C line
Find N and CPC for circuit and D/C those
Test L1 and L2
Test L2 and LN
Test LN and L1
Look for missed neons
Test Ln and L1
Reconnect and enliven.

If we left all the CPCs in the earth bar, and all the neutrals in the neutral bar, and the rest of the installation is turned on, then we are going to get very duff readings from where the Neutral and Earth are connected somewhere on the other side of the main isolator (PME, anyone?).

These are my thoughts, anyway.
 
No because the breaker would be open (off) and all the wires would be disconnected from the board altogether. All the other circs will be live, but the one I'm working on will be deader than dead.
 
Are RCD's/RCBO's able to with stand a 500V test ? I refer you to GN3 test 2 on page 38 which states that simple installations should be tested as a whole, and IF a reading of less than 2M ohm is recorded then the circuits should be tested individually
 
No because the breaker would be open (off) and all the wires would be disconnected from the board altogether. All the other circs will be live, but the one I'm working on will be deader than dead.
I'd always been told not to work on a board live, even taking the cover off, because it exposes live parts.
Any parallel paths should be taken into consideration because they will be present when the circuit is used.
 
IR is a dead test, surely??? I wouldn't fancy scratching around in a consumer unit with the busbar exposed if the thing wasn't proved dead!:D
 
The busbar wouldn't be exposed. The cables for the circuit would be disconnected as I keep saying.
Surely if this is the wrong way to test, there is no need to have access to the screw terminals in the top of an MCB, so why aren't they put behind the shield that covers the busbar.

Are you guys seriously telling me that if you replace a lighting pendant that you power down the whole installation? Or do you just not bother to test/certify?

And as someone else has said, I would be very dubious about putting 500V through an RCBO. I understand testing in many circumstances from the neutral and earth bars, but I have never seen or heard of testing from the line busbar in a consumer unit. It just seems like madness to me. What do you do if you find a fault, just say 'oh, there's a fault somewhere on the system. Oh well.'?
 

Reply to Insulation Resistance?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
481
M
  • Article
Heat resistant paste?? Hi guys What do you guys use when having to solder close to plastics? Are the pastes any good or not? If so, what products...
Replies
0
Views
126
macka09
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top