ogosh289

Hi all,

I've recently done the vrq level 2 and 2381 and have my assessment with Elecsa
in a few weeks. As I don't have a lot of experience with electrics I thought I'd
carry out some testing at home. When carrying out an insulation resistance test
(using a Mega 1553) on a ring final circuit i couldn't get a reading between
R1 + Rn. R1 + R2 & R2 + Rn both gave good readings >299M ohms. Previous continuity tests and polarity results were all good. I have removed every socket on the circuit and remade the connections, my next step will be to check the wiring between each socket back to the distribution board.
In my inexperience could I be missing something really simple? There are no Neons or anything else I can think of that may interfere with the readings.

Any advice would be greatly appreciated.

Regards,

Ogosh289
 
First off it's only continuity for R1 etc, for IR testing it's back to LINE/NEUTRAL/EARTH. What your saying that after the correct results for continuity and polarity you could not get a IR reading on the LINE/NEUTRAL. You did though get results on LINE/EARTH and NEUTRAL/EARTH.

IMO only one of two things can have happened

1) There as been a break in the cable between LINE/NEUTRAL since you did continuity test. But as you have said you checked the connections at each socket then that seems ok

2) You somehow did the LINE/NEUTRAL test wrong.

What I would do is find the first socket and disconnect it. Then find the leg that went back to the CU and IR test that. If you have it there then it is a case of going along the ring testing each point.
 
In addition to what malcolm has said i would have a really good look for something that you have missed that is still connected, if not a neon in the back of a cupboard in the kitchen maybe a fused spur off to the central heating or an outside light, etc have known it to be something in the loft before.
 
I am having a problem understanding the OP as well, the best thing to do is start at the beginning, cont test line, neutral, earth. do r1r2, r1rn, r2rn test at each point, then ir testing if others are all ok.

are you sure nothing is plugged in? under sink, behind dish washer, feed to shed, etc, etc.
 

Reply to Insulation resistance in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
240
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
That would depend on the instrument. On my old BM10 when you press & hold the button it just powers up the inverter circuits to generate the...
Replies
5
Views
426
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
440

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top