Insulation resistance | on ElectriciansForums
Discuss Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
sparky147
Hi just finnished installing 5 rcd sockets all rcd sockets are off, started my insulation resistance test, all sockets are conected and its disconected from the fuse board, got 500 m ohms from earth to neutral, 500 m ohms from earth to live, but when i test live to neutral i get a reading of 0.33 m ohms what can be the cause of this?
internal magical resistance bits inside the RCDs. try IR across one individual socket, isolated from yhr others.
there must be either something else plugged into the circuit or the RCD sockets, even when isolated are givng you a reading through the electronics of the circuit.
I have to be honest I don't think I have actually done an IR with an RCD socket connected, I have always disconnected them, as even if I did the test at 250V I would be worried of damaging them. Try and disconnect the sockets, and chocy block the cables and re-test.
Most RCD sockets don't like insulation tests and come with a consumer unit warning sticker. The installer is supposed to disconnect them before testing....
Reply to Insulation resistance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Thank you for your help. Will double check everything tommorow and try to find out what was on at the time of tripping. Still need to retest the...