So strange, R.C.D. DOES NOT TRIP!
Hardly strange, given that you have a resistance of 350,000 Ohms.
Therefore less than 0.0007A will flow. The RCD needs nominally 0.03A
Hardly strange, given that you have a resistance of 350,000 Ohms.
Therefore less than 0.0007A will flow. The RCD needs nominally 0.03A
So when you do an insulation res. test before fitting an R.C.D. what minimum value would you be looking for?
Also would this now suggest my pond pump is on its way out or letting water in?
So when you do an insulation res. test before fitting an R.C.D. what minimum value would you be looking for?
Also would this now suggest my pond pump is on its way out or letting water in?
Surely with the 2391 under your belt this is stuff you should know !
a reading over 1Meg. is acceptable, but it's good practice to investigate anything under 2 Meg. the pond pump could just be moisture in an adaptable box or outdoor socket.
Yeah i know that of course. But if you add an RCD you are making the safety alot better you can't be held liable for a fault already in place. You could advise the customer and charge to correct it, surely?
Doing an IR test with loads still connected is always going to end in tears.
a lot of electronic gear has earth leakage. always disconnect before testing. as cpl. jones famously said " they don't like it up'em".
What you've discovered is that the earth is functional as well as protective. Depending what test voltage you use to mega test all surge arrestors will show as low insulation.
A surge arrestor would see 500volts as a surge which it would allow at least a portion of the waveform to pass safely to earth. It's possibly a good job there were surge arrestors left plugged in because you're likely to damage electronics if you run around IR testing at 500 volts on circuits with appliances still connected. I'd count myself lucky and do some more reading on correct testing procedures if I were you.
This is basic stuff really.
Test IR at 250v first, 90%+ of low readings are due to appliances plugged in and always go round and unplug EVERYTHING, some sockets are SP isolators, as are some FCU's.
Never fire 500V at a circuit with really low IR unless you are 100% certain everything is unplugged.
And yes I mean test the circuit in question only, all 3 to each other.