Jamieblade1

Hi guys,

I've recently just completed a rewire of a small 2 bed bungalow consisting of 4 circuits. I have tested the kitchen ring and it has tested fine, the same with the lighting circuit. On testing the heating circuit and general ring main, the insulation resistance between L-N on both circuits is 0.3 Mohms. Between L-E and N-E they test fine at over 200Mohms. I have looked for the obvious i.e nails through cable in capping etc twists and kinks in cable. The cables move freely in the capping when pulled. The 1.5mm supplying the fused spur in loft for the heating is no longer than 6 meters in length. The general sockets however, I have split the ring down to find the leg which is causing the low reading and it seems to be the supply from the consumer unit to the first socket. But as I've said there are no nails, plaster, clips or anything on the cables. Really frustrating now, especially as the bungalow has just been skimmed!

Any chance it could be faulty cable?

Any help will be greatly appreciated.

Cheers
 
If your 'low' reading is L-N there will be a load connected somewhere......hopefully 500v up it's jacksie hasn't trashed it.
Usual missed culprits are heating controls,neons and tv amps. 0.3 megs is also typical of a surge protected lead.
 
Heating is likely to be the Neon on the FCU.

With the socket circuit, disconnect both ends of the leg you think is the issue, if it is the leg that goes from c.u. to first socket (like you think) and still has poor reading - no other option other than to replace
 
Last edited:
There are no loads connected and FCU's are non-neon. Basically just a 1.5mm up to a FCU with about a 6 meter length for heating, that's it, no combi fitted as yet. The property is completely empty.
 
100% nothing connected whatsoever, the heating goes straight from CU to FCU with no load (no combi fitted) and the first leg from the CU to the first socket also reading the same L-N, 0.3mohms
 

Reply to Insulation Resistance in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
227
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
638

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
323
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
270

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top