Insulation resistance testing hasbeen carried out on a installation in a shower block and the followingresults obtained

live to live = 200m ohms
live to earth = 0.5m ohms

a. are these testresults are acceptable:
b. The actions to be taken should thetest results be unacceptable are:
 
Anything above 1mohm is acceptable, although I personally would like to see more than that.

Providing you have disconnected all sensitive equipment, then you have an issue with the insulation breaking down between live and earth. The section of cable at fault will need to be replaced.
 
Has as been said the result look poor live earth have you checked for neons if their is one then it will need to be isolatted so have a good look round see if their is one the retest with it isolatted
 
yes. because you are leaving a load with a finite resistance across L and N.
 
Yes but a neon would not be across line and earth, unless its been installed by a cowboy.
Not sure of the effect of a neon, as IR tests are done with DC........

In any case, Paul.
This is obviously a college exam question, so you should be able to come up with an answer first. We could then give you some guidance. You'll not learn by just asking without making any effort.

*CLUE*
Have a look in BS7671 in teh section on IR testing and what the acceptable IR limits are. then you could come up with an informed answer.
 
so basically the actions the need to be taking is they needs investigating to find what is causing the results to be low. which something such as neons not disconnected before test. if we find what we think is causing it we need to disconnect it and do the test again until we get the reading over 1 mega ohms
 

Reply to insulation resistane testing please help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top