ive a lighting circuit with a 12v transfomer (fan), about 8 high..ish fluorescents and a bathroom with pir controlled ballast fluorescents approx 6 if i remember


now to insulation test, is it easy as joining the live and neutral together at the dist. box and test between them and earth, other than that its a heck of alot of disconnecting!!
would the pir handle it?

i've never needed to use this method, an i dont fully quite understand how it wont blow a ballast, or electronics?

thanks
 
Yes, test IR with L-N joined, as the L-N are shorted the electronic circuitry will not see a potential difference, the only proviso is, if there any functional earths (e.g. RCBOs and telecoms equipment) these will need to be disconnected. Note on the paperwork that IR test carried out L-N joined.
You will only need to remove lamps, bypass PIR sensor and isolate the fan and it's transformer, if the previous test reveals low insulation <2M Ohms, when you will need to carry out a full IR test, between live conductors and between each live conductor and earth.
 
Last edited by a moderator:
If it's a standard ballast it should survive an IR test with the L+N connected together. If the ballasts are addressable with serial comms such as DALI then the comms system might use 0v earth referencing in which case any IR test even with the L+N connectec will cause damage. Same goes for some EPOS systems. I would refer to manufacturers data sheets for advice on insulation testing.
 
Yes, test IR with L-N joined, as the L-N are shorted the electronic circuitry will not see a potential difference, the only proviso is, if there any functional earths (e.g. RCBOs and telecoms equipment) these will need to be disconnected. You will only need to remove lamps, bypass PIR sensor and isolate the fan and it's transformer, if the previous test reveals low insulation <2M Ohms. Note on the paperwork that IR test carried out L-N joined.

Why remove lamps?
 

Reply to insulation test on sensitive equiptment in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top