DaveW

Hi,

Before starting to add a couple of sockets to an existing ring in a kitchen, I did the dead tests on the circuit. Insulation test gives me 0.3meg L to E and N to E,with 500ohms L to N. Any ideas on what I have missed switching off, just hope it is not the wiring. It looks as though someone has been playing with it!
 
All loads from circuit need to be removed and do you have any neons in the circuit they will play havoc with your readings.


Chris
 
Fridge into a hidden socket?

Trailing extension with something left in, often thrown up ontop of wall units but out of eye-shot?
 
When you get this situation do a test with live and neutral one one clip and earth on the other if reading is ok then you definitley have something on the circuit that should not be there.


Chris
 
check it on continuity see if you get a reading ,if you do go round the sockets one at a time the readings should increase the further away and de crease lower the reading closer you are to the plugged in appliance or fault ,may not work but worth a try ,i use this method when the readings are zero , and once ive cleared the fault etc i re do the IR test
 
Hello,

Thanks for your help, I used a combination of all your suggestions. It is amazing how many sockets are behind cupboards and forggoten, no matter how many times you ask are there any more things connected. TV aerial amplifier and a surge protector hidden under a pile of clothes.

Meter reading is now greater than 500meg.

Thanks

DaveW
 

Reply to Insulation test problem. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

  • Question
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
Replies
7
Views
672
davesparks
D
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
587
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top