G

gravitate

What I have been told to do is test a bunch of thermocouples at work. The equiptment I am using is shown here http://www.hkanswers.com/testing.jpg

These are my questions. I am testing them at 250v and if I get a reading less than 1 giga ohme or 1000 mega ohmes Then I take it as needing replacing. Does this mean that they are dangerous i.e. if you touch the stainless sheath you will get a shock? Also does this mean that if I do a continuity test from the wires to the thermocouple then I will detect a current?

Also Please can someone tell me how to do a loop resistance test? I have been told that when I do a loop resistance test I should get no more than 17 ohmes/m
Please could you describe how to do it in detail as I am not electrically minded and dont know any jargon.
Many thanks
 
The meggar will give you that 250v test on IR.

Being a non megger man and the picture is a little blured I can't see the scale :eek: this old age don't come on it's own it brings all it's friends along like dodgy mince pies.

But for the loop as you say set the meter to the continuity/ohms scale and then croc clip one on the green/white and the other on the blue/white and just read the screen
 
great thanks for that. Regarding the loop resistance test then am I right by saying that turn it to the ohmes scale as you say then put the terminals on the wires that come from the thermocouple?
 

Reply to Insulation testing and Loop testing of Thermocouples in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
1K
When working in the motor repairs industry you have to fill in test sheets and keep them for so long. Doing that will do is ok for most things but...
Replies
10
Views
3K
  • Question
Tim - shear brilliance mate
Replies
12
Views
1K
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
Replies
24
Views
3K
  • Question
Interesting item you have there. This blog might be worth a read https://sllipblog.wordpress.com/2014/04/29/its-now-00-28am-and-i-need-my-bed/...
Replies
9
Views
406

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks