Piratepete

Hi Guys

Domestic - Old Hager Box 14 MCBs RCD Main Switch. Totally stuffed with wiring - not keen to disturb

Tested the Full L+N busbars to E. IR = 1.8 Meg b****r! So close to 2 Meg!

Tried L busbar to E -all trips off. 1.8 Meg!!!!!!!!! - had to disconnect RCD!

Tried each cct in turn L to E. Five of them reduce IR to about 1.8 Meg. Obviously a nonsence!

I'm theorising that one cct has a low IR Earth to Neutral and I'm seeing feedback through these other ccts which may have something connected/switched on.

Is the only way that I'm going to solve this problem going to be to disconnect the Neutrals one at a time to try and find a cct with low IR?

Cheers
Pete
 
Sorry mate if this is not what you wanted to hear, but you need to IR test each circuit separately. Remove or isolate all loads. Initially, test each isolated circuit one at a time with the neutrals commoned. Only if your results still suggest a common fault to several circuits would you need to separate the neutrals and retest.
 
Last edited by a moderator:
Your 1.8meg, on the whole installation, is due to resistances in parallel. You will have to disconnect each circuit as stated earlier, and see what effect that has. With 14 circuits, my best guess is that if you do them individually your readings will come back into spec at 2 meg plus. If one circuit is low and pulling down your resistance total value, then you will find it fairly easily.

Cheers............Howard
 
Last edited by a moderator:

Reply to Insulation Testing Conundrum in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
You too? I thought I was in a unique position:anguished::coldsweat:
    • Like
Replies
5
Views
266

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top