Hi Guys
Domestic - Old Hager Box 14 MCBs RCD Main Switch. Totally stuffed with wiring - not keen to disturb
Tested the Full L+N busbars to E. IR = 1.8 Meg b****r! So close to 2 Meg!
Tried L busbar to E -all trips off. 1.8 Meg!!!!!!!!! - had to disconnect RCD!
Tried each cct in turn L to E. Five of them reduce IR to about 1.8 Meg. Obviously a nonsence!
I'm theorising that one cct has a low IR Earth to Neutral and I'm seeing feedback through these other ccts which may have something connected/switched on.
Is the only way that I'm going to solve this problem going to be to disconnect the Neutrals one at a time to try and find a cct with low IR?
Cheers
Pete