I had a customer call me out yesterday and here is the script.
Thety move into the house 3 weeks ago,
since they moved in the RCD on the high integrity CU (main switch with 5 MCB's and RCD with 5 MCB's)
has been tripping regularly. (upto 3 times in one day)
The most comon time the RCD has been tripping has been around 3am but it has been tripping during the day and evening.
I look around the premises for an outside light that mayb egetting damp and causing the tripping, however the outside light was on the lighting circuit (on the mainswitch side of the CU)
On the RCD side of the CU I found the following circuits
cooker 6mm cable 32amp MCB
on 500v range on insulation resistance test >500M ohms between Nuetral and earth
power radial
2.5mm cable 16amp
on 500v range on insulation resistance test >110M ohms between Nuetral and earth
power radial (2 radial circuits bunched on one MCB)
2.5mm cable 32amp
on 500v range on insulation resistance test >115M ohms between Nuetral and earth
Trip load on RCD was 27mA @ 7.6ms
this was a 30mA RCD
The customer had a new fridge delivered a bout the time they moved into the house, so I suspect that it maybe the fridges compressor tripping the RCD.
For test purposes I moved the Fridge onto a spare 6amp MCB on the non RCD side of the CU so that we eirther confirm a problem with the fridge or not.
Basically I think the Fridge compressor maybe tripping the RCD
I didn't have my PAT test equipment with me so when I return I will PAT test the fridge
any thorghts anyone?
Thety move into the house 3 weeks ago,
since they moved in the RCD on the high integrity CU (main switch with 5 MCB's and RCD with 5 MCB's)
has been tripping regularly. (upto 3 times in one day)
The most comon time the RCD has been tripping has been around 3am but it has been tripping during the day and evening.
I look around the premises for an outside light that mayb egetting damp and causing the tripping, however the outside light was on the lighting circuit (on the mainswitch side of the CU)
On the RCD side of the CU I found the following circuits
cooker 6mm cable 32amp MCB
on 500v range on insulation resistance test >500M ohms between Nuetral and earth
power radial
2.5mm cable 16amp
on 500v range on insulation resistance test >110M ohms between Nuetral and earth
power radial (2 radial circuits bunched on one MCB)
2.5mm cable 32amp
on 500v range on insulation resistance test >115M ohms between Nuetral and earth
Trip load on RCD was 27mA @ 7.6ms
this was a 30mA RCD
The customer had a new fridge delivered a bout the time they moved into the house, so I suspect that it maybe the fridges compressor tripping the RCD.
For test purposes I moved the Fridge onto a spare 6amp MCB on the non RCD side of the CU so that we eirther confirm a problem with the fridge or not.
Basically I think the Fridge compressor maybe tripping the RCD
I didn't have my PAT test equipment with me so when I return I will PAT test the fridge
any thorghts anyone?