Visited a property today that has an intermittent earth fault. RCD trips sometimes 3 times a week sometimes once a month but it's been going on for some time now and owner wants it sorted.

IR'ed across N/E and L/E and all ok until the boiler is switched into circuit. Then the L/E values dip to under 0.1M ohms on all but one of the 5 circuits on the RCD.

Would you expect to get such low readings across L/E on a 2 year old boiler? I would of said not but perhaps I'm missing something. I've got to go back tomorrow with plumber so any advice or comments would be most appreciated. Install is approx same age as boiler.
 
Hi

Is the rcd part of a split consumer unit?? lookout for borrowed neutrals and outside lights or sockets?? I had a problem similar and it was the pir light at the back door everytime it rained

You also get leakage currents from most appliances in an installation and sometimes they all total more than 30ma and cause rcd to trip

Can you swing the suspect boiler supply onto the non rcd side of the board?? and try it for a week??

hope this helps you? one of the hardest faults to find??
 
Boiler is spurred from kitchen ring (doh!). C.U. is split load (16th Ed), all lights on non RCD side as is oven/cooker. No spare ways even it was possible to re-wire boiler on own circuit (which it would appear it's not). Probably gonna have to call in boiler man and see if he can find boiler fault, if not it's back to square one.:(
 
Hi

Might be worth while running temp supply from socket outlet on CCU for 1 week then you can say for def??
Also check RCD I had one that was faulty (Wylex) and was tripping intermittently at strange times normally through the night when I tested at 50% 15ma it was tripping but it had been ok for first 3 weeks in use
 
Not too familar with the Worcester conventional boilers with regard to faults they may have but have you checked the motorised valve on the hot water tank feed had a few intermittant faults on them over the years when they operate
Also the circulating pump depending which type is fitted can cause problems as they have water in the main body
 
As with all intermittant faults it is trying to recreate the A+B+C operation that causes the fault

Does the fault occur at different times or similar times each time it trips out
 
had a similar job a while ago, and it was down to the boiler.
As jibjob has done, i proved the wiring upto the boiler was good and fault free, and had to simply hand it back to the client with a contact number for a local friendly boiler engineer i knew..
never found out what it was other than an internal fault with boiler.
 
Been back with plumber, checked pump, boiler, motorised vales etc still no joy. Trouble is, the RCD may not trip for another 2/3 weeks and then were back to square 1. Gonna suggest I install seperate circuit for boiler (shouldn't be to difficult as they're in close proximity of each other) and move onto non-rcd side of board (spare ways permitting). Then we'll see what happens. Of course it could be nusiance tripping but try telling that to the person that has to live with it. Fun & games eh.
 

Reply to Intermittent Fault Headache in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
830
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top