Visited a property today that has an intermittent earth fault. RCD trips sometimes 3 times a week sometimes once a month but it's been going on for some time now and owner wants it sorted.
IR'ed across N/E and L/E and all ok until the boiler is switched into circuit. Then the L/E values dip to under 0.1M ohms on all but one of the 5 circuits on the RCD.
Would you expect to get such low readings across L/E on a 2 year old boiler? I would of said not but perhaps I'm missing something. I've got to go back tomorrow with plumber so any advice or comments would be most appreciated. Install is approx same age as boiler.
IR'ed across N/E and L/E and all ok until the boiler is switched into circuit. Then the L/E values dip to under 0.1M ohms on all but one of the 5 circuits on the RCD.
Would you expect to get such low readings across L/E on a 2 year old boiler? I would of said not but perhaps I'm missing something. I've got to go back tomorrow with plumber so any advice or comments would be most appreciated. Install is approx same age as boiler.