When carrying out the test mentioned above what do you guys find the easiest and quickest when doing it on the whole installation ?
 
Main switch off, all mcbs on, link N bar to one mcb, 250v IR between N bar and E bar If all clear then again at 500v If a low reading then I first switch off each MCB at a time to try narrow the low reading down.


Edit, oh and if the propertys ocupied then i note as a limitation that no IR was taken between line and neutral.

Note: this is shown in its basic form and other things relating to safety and protection are carried out. :)
 
Last edited by a moderator:

Reply to IR between live conductors & Earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

As you've found out, there's capacitive coupling between cores which will induce a voltage into other cores when one (or more) is fed with AC. How...
Replies
3
Views
394
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top