Hey Guys

I've got a bit of a head scratcher that I was hoping someone could help with.

I have a ring main feeding 7 points. When testing IR btw L&N I get 967Mohm but when testing N-E & L-E I get 455Mohm. I split the ring and tested as 2 radials and the results suddenly come back all clear at >1000Mohm L-N L-E and N-E??? When I reconnect the ring it's back down to 455Mohm??

I've checked all connections at the sockets and all good.

Any ideas??

Cheers
Mark
 
Are you disconnecting ALL the circuit conductors from the CO Ls, Ns and cpcs??
 
Actually, looking at the figures again.
If you have about 500M IR for a complete ring, then splitting into two halves would give about 1000M for each half if the 'fault' is evenly distributed.

I don't really see a problem, especially as the figures are so high.
 
I'd agree the values look ok. The L-N us passing through two conductor insulations. L-E and N-E are only passing through the line conductor insulators as the CPC is bare.
A little moisture in the cable and you will see lower values.
Your tested proved the values where consistent even when split.
 
the only problem as i see it is OP considering that 455Mohms is worthy of a second look. many MFTs only read up to 299Meg.
 
the only problem as i see it is OP considering that 455Mohms is worthy of a second look. many MFTs only read up to 299Meg.
probably a strange thought, but any chance the OP could be misreading the MFT and stating OHMS instead.
 

Reply to IR connundrum in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
831
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
736

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top