Hi guys,

What plug in equipment, if any would show a dead short when doing an ir test?

I have the line and neutral connected together and testing between that and the earth bar.

The circuit was energised and working fine on arrival (doing an eicr) so it cant be an actual dead short or the mcb would have tripped.

The circuit im testing is a 16a 2.5 radial that feed sockets in various rooms some of which are ceiling high with crap so something could be plugged in and i wouldnt even know.

Cheers,
Tim
 
Could be anything, usuall what I find is fused connection units supplying deaf loop, intruder alarms, small P.S.U's etc.

Are you carrying out the test between LN-E and are still getting 0.00MegOhms? Can you be sure it is correct neutral mate.
 
I have the line and neutral connected together and testing between that and the earth bar.

The circuit was energised and working fine on arrival (doing an eicr) so it cant be an actual dead short or the mcb would have tripped.

If it's a short between neutral and earth, it won't trip the mcb, but will show up on a 'L+N to E' IR test.
 
If you are getting 0.0 Mohm then try a continuity test to see if you are missing something, if you get a reading in ohm then it is probably something about your testing method.
If there is another circuit crosslinked to this and the main switch is on then you will get 0.0 Mohms.
If you are getting say 0.5 Mohms then you are likely to have a power supply connected.
The other thing to try is test at 250V and see if the result is OK, then it may be a plug in surge protected socket.
 

Reply to IR method 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
453
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top