When testing IR on a 3 phase and N where the N cannot be swiched is it considered safe practice to disconnect the incoming N from it's stud
Pict
 
IMO only if the board is totally isolated. and even then, treat it as a live conductor.
 
IMO, if the entire installation is safely isolated and all electronice equipment is disconnected (I'm thinking emergency lighting here) there should not be any current flow in any of the line conductors ergo there shouldn't be any return current flow in the neutral conductor.

For safety's sake I would terminate the supply neutral tail into a connector block of some description for the duaration of the test just as an added precaution.
 
I use one of those all plastic spring clamps, I can get the bared copper completly enclosed, I was just wondering what the "offiical" line was and GN3 says nowt about it, I might run it past my NICEIC area rep although it will probably be a case of what we in Scotland call "skelfs in the erse" from sitting on the fence
Pict
 
You are always going to get a 'dead short' reading if it is TNC-S (PME) any how. Years ago when I worked for hydroboard it was common practice to fit a swivel link on the neutral along with the earth. We were always taught to carryout IR on circuits before final connections to DB's
 
The neutral has to be disconnected to do the N-E IR test. Personally I would disconnect and immediately do the N-E test and then reconnect the neutral.

The reason for my method, if there are downstream single phase circuits and you forget to reconnect the neutral. And then close the 3 phase switch you will put 400v across the single phase loads. And you would not be very popular if you did that.
 
Many Many years ago I was fitting a single pole MCB to a three phase board which was in a cupboard full of junk I knelt on a table leaned across some boxes and fitted the breaker, but caught two prongs of different phases, jeez what a bang, I took out the isolator and vapourised the copper prongs, just because they did not want the power of during lunches, I learnt a two valuable lessons one I am not immortal and two safe isolation is done for a reason. So Oxo your right, your only popular if no one knows you even in the building.
Pict
 

Reply to IR on a whole board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
592
loz2754
L
Hello All, This is Vaithees from India. We are using an IR heater for a vacuum & non-vacuum chamber and got a heater from Chinese company and its...
Replies
0
Views
271

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top