Hi people!

Right just done a CU swap, tested all circuits and ok, did the IR L-E, N-E on the upstairs lights and got the reading of 0.29MOhms and 0.24.

Have got no idea on where to start looking for faults or disconnecting? Should i be taking bulbs out? transformers for downlighters in bathroom? Pretty sure its all ok as RCD is fine and house is 15 years old so not old wiring.

tester is ok as used for all other circuits.

Need some help please people!!!!!!!!!! ASAP!

Jason
 
You answered all your own questions when doing IR all loads should be disconnected, including smoke alarms transformers, neons etc.
 
so you think taking out all the lamps will rectify results? Didnt do this downstairs or on other CU changovers and results were good?
 
Hi people!

Right just done a CU swap, tested all circuits and ok, did the IR L-E, N-E on the upstairs lights and got the reading of 0.29MOhms and 0.24.

Have got no idea on where to start looking for faults or disconnecting? Should i be taking bulbs out? transformers for downlighters in bathroom? Pretty sure its all ok as RCD is fine and house is 15 years old so not old wiring.

tester is ok as used for all other circuits.

Need some help please people!!!!!!!!!! ASAP!

Jason

Yes you must remove lamps, dimmer, not test throu RCD etc, retest, once you done this, if still low, inspect flex between ceiling rose and lamp holder.

As for fault finding the 50/50 method is the best, first remove neutral, earth and switch breaker off for line, then roughly divide the circuit up 50/50 at that oultlet split the line neutral and earth and test each half this should eliminate 50% of the circuit from fault finding. if one half give you a low reading subdivide that half again, and so on.

I do suspect over heating or insulation damage (loose connection) could be cause of you low insulation, so as previously stated check all lampholder also in vestigate if ther could be a junction box or similar joint in the ceiling.

May be check termination entering board, have had experience where insulation has been damaged by metal enclosure or knife cutting throu insulation showing bare copper, then moisture damp shorting out conductors or it could just be because of the age of the wiring, inspect it all, I had person connect PVC to VIR etc.

Personnelly I alway perform PIR inspection and test of the electrical installation before any board changes, yes it add time and cost to the board change, but it save me a lot of hassle and addition cost in the long run.

You could be in a position where the lights needing rewiring and a client unwilling to pay for it, and do not leave it as you changed the board and have to issue test cert with you name on etc, it could work out very expensive if sued/prosecuted, I hope not.

Best of luck and let us know how you get on.
 
Last edited by a moderator:

Reply to IR on upstairs lighting in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
758
  • Question
What @Avo Mk8 suggests crossed my mind. Try an IR test at 500v.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top