Hi guys job today for nuisance rcd tripping ,I thought it was an appliance as I explained in a post yesterday but turns out it wasn't . Anyway disconnected the only neon I could see , unplugged everything run an IR test ,great neutral to earth but earth to live 0.02 . Checked every socket , I found a few oxidised cables and gather there's a few joins due to single cables at various sockets . Would there be anything I'm missing that would give me a reading of 0.02 ? I realise with the oxidised cables it should be rewired but I got a perfect reading on the earth to neutral and would presume if the cables had deteriorated that much surely it would of affected them all in some way ?
Also tried a ramp test but it would instantly trip ?
any ideas would be much appreciated .
thanks to any replies in advance