C

chopper

out of interest , if a DB is fed with armoured cable using the starnds as earth which is fed from a main isolater which is on a TNCS supply, to carry out the IR would i have to dissconnect the neutral out of the main isolter ( not on the DB ) and the earth fly lead off the banjo. when testing N to E. WoULD I ALSO have to dissconect the fly leads from the rcbo ( earth and neutral ) then i could simply test from load side of rcbo to earth terminals.
doing the above this would mean i could also test L TO N on load side of rcbo
and L to E stRAIGHT FROM LOAD SIDE OF rcbo and earth terminals

am i thinking right, i went to job today gaffer says me and him will be testing it so i was trying to think on how he would probly do it for the best way, it was a 16 way 3 phase so be loads to dissconnect
 
When IR or loop testing all RCBOs with a functional earth wire require this flylead to be disconnected during testing. Some manufacturers additionally require the neutral flylead to be disconnected and/or the RCBO switch dolly(s) in the OFF position during testing. Check the manufactures instructions, as not following their instructions risks possible misleading results and/or damage to the protective device.
 
Last edited by a moderator:

Reply to IR teating when RCBOS are in place in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
830
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

  • Question
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
Replies
7
Views
675
davesparks
D
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
380

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top