Stever_777
If I test as in my title on an old board, what reading should i get that will not start tripping an new Rcd board
Steve
Steve
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss IR test @ 250V across N & E bars? in the Australia area at ElectriciansForums.net
You should test @500v....and a reading >1mohm should be obtained,if you are testing @250v to avoid damage to connected equipment you should note the departure on the cert,minimum reading is the same.But it is likely that a reading taken @250v will decrease @500v so is not a reliable indicator of trur IR.
Readings much lower than 1meg will not cause nuisance tripping generally....remember a few years ago the minimum was 0.5megs.....I would only expect problems with readings <0.4megs. Such low readings will not comply with the regs though and should be improved.
If I test as in my title on an old board, what reading should i get that will not start tripping an new Rcd board
Steve
Use ohms law.
230/0.03 = 7667 ohms. = 0.007667 Mega-ohms (assuming 30mA RCD)
So, transposed, any resistance value less than that will cause the device to operate.
Reply to IR test @ 250V across N & E bars? in the Australia area at ElectriciansForums.net