If I test as in my title on an old board, what reading should i get that will not start tripping an new Rcd board

Steve
 
You should test @500v....and a reading >1mohm should be obtained,if you are testing @250v to avoid damage to connected equipment you should note the departure on the cert,minimum reading is the same.But it is likely that a reading taken @250v will decrease @500v so is not a reliable indicator of trur IR.
Readings much lower than 1meg will not cause nuisance tripping generally....remember a few years ago the minimum was 0.5megs.....I would only expect problems with readings <0.4megs. Such low readings will not comply with the regs though and should be improved.
 
Last edited by a moderator:
You should test @500v....and a reading >1mohm should be obtained,if you are testing @250v to avoid damage to connected equipment you should note the departure on the cert,minimum reading is the same.But it is likely that a reading taken @250v will decrease @500v so is not a reliable indicator of trur IR.
Readings much lower than 1meg will not cause nuisance tripping generally....remember a few years ago the minimum was 0.5megs.....I would only expect problems with readings <0.4megs. Such low readings will not comply with the regs though and should be improved.

If I test between live conductors and earth then my readingis going to be more reliable.
 
If I test as in my title on an old board, what reading should i get that will not start tripping an new Rcd board

Steve

Use ohms law.

230/0.03 = 7667 ohms. = 0.007667 Mega-ohms (assuming 30mA RCD)

So, transposed, any resistance value less than that will cause the device to operate.
 
Last edited:

Reply to IR test @ 250V across N & E bars? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
376
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top