S

Stever_777

If I test as in my title on an old board, what reading should i get that will not start tripping an new Rcd board

Steve
 
You should test @500v....and a reading >1mohm should be obtained,if you are testing @250v to avoid damage to connected equipment you should note the departure on the cert,minimum reading is the same.But it is likely that a reading taken @250v will decrease @500v so is not a reliable indicator of trur IR.
Readings much lower than 1meg will not cause nuisance tripping generally....remember a few years ago the minimum was 0.5megs.....I would only expect problems with readings <0.4megs. Such low readings will not comply with the regs though and should be improved.
 
Last edited by a moderator:
You should test @500v....and a reading >1mohm should be obtained,if you are testing @250v to avoid damage to connected equipment you should note the departure on the cert,minimum reading is the same.But it is likely that a reading taken @250v will decrease @500v so is not a reliable indicator of trur IR.
Readings much lower than 1meg will not cause nuisance tripping generally....remember a few years ago the minimum was 0.5megs.....I would only expect problems with readings <0.4megs. Such low readings will not comply with the regs though and should be improved.

If I test between live conductors and earth then my readingis going to be more reliable.
 
If I test as in my title on an old board, what reading should i get that will not start tripping an new Rcd board

Steve

Use ohms law.

230/0.03 = 7667 ohms. = 0.007667 Mega-ohms (assuming 30mA RCD)

So, transposed, any resistance value less than that will cause the device to operate.
 
Last edited:

Reply to IR test @ 250V across N & E bars? in the Australia area at ElectriciansForums.net

Similar Threads

  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
975
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
662
  • Question
It can also mean lasts or continues for two years.
Replies
14
Views
890
  • Question
take all the neutrals out of all the neural bars (mark them first) puts wagos on each one and power up the offending circuit,any neutrals...
Replies
6
Views
2K
  • Question
Mice are one option, as in they might have nibbles both L and N over a segment, but most circuits seemed OK so far and no other evidence of an...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks