Could anyone please advise on a IR (250V) reading of 0.02MΩ on the permanent live of an emergency lighting circuit to earth ONLY. Lamps have being removed, but ballasts and batteries are still in circuit? The breaker is mechanically sound and stays on with this apparent dead short to earth? Could it be the batteries in the fittings because the switched live on the circuit is clear?

Thanks for reading!
 
Last edited by a moderator:
0.02Mohms is 20Kohms. this is probably due to the ballasts in the fittings.a 5mA leakage. i would disconnect the fittings and test again, or accept the readings.
 
Last edited:
Thanks for your quick response! The strange thing is, the switched live is clear but it's the permanent that reads as down to earth. Could it possibly be the battery and not the ballast due to the switched live being clear?

Thank you.
 
not the battery itself, but its associated charging circuitry. anything electronic is liable to show leakage. as long as you are happy with the wiring. then it's fine.
 
If you've got such a concern about this why don't you connect the incomer to the out going leg at each fitting using a lever wago (for speed) and test at 500V?
 

Reply to IR test on 110v emergency lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
2
Replies
15
Views
942
nicebutdim
N
If it's going to be an emergency stop and not just a stop, then other factors come into play depending on what sort of machines the emergency stop...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top