Cor, I didn't expect the Spanish Inquisition.
Job was additional lighting point on upstairs lighting circuit, and a spur to new double socket (protected by RCD FCU) on upstairs sockets. Problem was that the CU internals was a proper stuffed-in spaghetti job - no rhyme or reason to the conductor positions in the earth and neutral bars, and a complete pain in the backside to get any of them out and back in again even if there had been, and risk of doing more harm than good in trying. This will not be that unfamiliar a scenario to anyone who does a sigificant amount of domestic work, I suspect.
So I elected to do whole-installation (L+N combined)-E testing at 250Vdc, to allow for connected equipment, followed by live test for polarity (including switching being of the line conductors) and Zs at the new lights and sockets, plus a Ze test at the CU (earthing conductor out) to check the source of earthing.All of my new wiring I tested at 500V between all conductors with CPCs connected to earth prior to final wire-in to the existing circuits.
Yes obviously if the result is a big fail then you can end up chasing your tail, and functional earths (e.g. on RCD protected sockets/FCUs) and filter networks can cause said big fail, but if it isn't then it's happy days...?
At risk of stating the obvious, testing L+N combined to E at 250Vdc does not inject any voltage between L and N and so nothing is getting supplied L-N with 250Vdc. This is the same as an IR soft PAT test. I wasn't inclined to spend forever running round the house in advance unplugging, switching off FCUs, taking out bulbs, removing neons and dimmers etc. etc. and then missing something anyway. Didn't test L to N as connected loads would have caused test to fail and exposed items to the test voltage L to N.