Hi all

IR test at outgoing terminals on main switch on splitload wylex board. All mcb's and both RCD's up. L>E 275k ohms. Limitation in place not to test between L>N, Opinions please.

Cheers
 
I don't get it...opinion on the reading?...well there could be a problem or there could not...who knows without further testing...

You've done a global IR test and got that result?...so carry on to your next step?...
 
I'm guessing this is for an EICR as you have mentioned 'limitation'. Also I'm assuming that when you say 'up' you're implying 'on' or 'closed'.

You have found 0.275MΩ between L-E on a global IR test which is less than 1 so is not acceptable and is a code. If you are doing an EICR then I would be doing the same test for each circuit as you will need these results for 'form4' and then you will see where the culprit is.
 
Hi all

IR test at outgoing terminals on main switch on splitload wylex board. All mcb's and both RCD's up. L>E 275k ohms. Limitation in place not to test between L>N, Opinions please.

Cheers

My opinion is do you know how to test properly ???
Do you think you should be testing "each" circuit to find the culprit or are you one of these test 20 houses per day grab your money and bugger off mickey mouse sparks ???
By asking this question you are obviously not competent to test and certify peoples houses!!
 
Dear oh Dear oh Dear
 

Reply to IR test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
349
Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
461
TerryBNZ
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top