Can anyone give me some advice on Insulation Resistance Testing a domestic install by means of 'Back Testing' at a socket outlet. I'm writing this with regard to MW and PIR - As a retired Sparky told me recently that if i test between L&E then N&E with all Fuses in or Mcb's on in the CU (disconnect any rcbo's or rcd's in the install) and turn OFF the main switch, then this will test the entire install in one hit & as long as the readings are above that stated in BS7671, then all ok. Does this method get used much? I can see the advantages as no need to remove lamps and appliances with plug tops, just need to check switches for strapers and test again. I would'nt do an IR test between L&N with this method of course, just record it as a LIM on the results (due to not knowing what the customer may have connected & maybe no access). I understand this way of testing would be no good on a new install when doing an EIC, just looking at using this for MW & PIR and also for previewing any work before quoting an install to give an idea of what the IR may be like. I've not used this method before, anything i should keep in mind before i try it out that i might have overlooked. Many Thanks in advance.
 
i cant see any reason why this wouldnt work, but surely, one of the places you would want a decent look at during a PIR/EICR is the CU/Fusebox. for that reason i would do it then. Also i wouldnt just do the L-E and N-E, unless i couldnt disconnect everything. the tip to checking for connected loads is to test at as close to operating voltage first. ie, if your testing 1ph, then test at 250 before upping to 400. you will notice that any connected loads will give low readings
 
I have only heard of this from 1 other person. For 99.9% of the time it will never work. I can't remember the last time I could turn off a whole install and do continuity and IR test.
Better off doing it at the DB.
 

Reply to IR Testing Domestic install by Back testing at a socket outlet in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
Replies
7
Views
558
davesparks
D
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
925
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
978
Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
Replies
17
Views
3K
Replies
1
Views
628

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks