IR Testing lighting cct with fixed bathroom extractor load | on ElectriciansForums
Discuss IR Testing lighting cct with fixed bathroom extractor load in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
F
freedomrun
Domestic CU change, TN-C-S. Lighting circuit has an Extractor Fan with Electronic timer installed. When performing IR test on the lighting, should i just test the whole lighting cct between L & N (connected together) and the CPC - I do not want to remove the cover of the extractor to disconnect at the terminals as i may damage the plastic housing. If i do the IR test in this way, should i make a note of it on the EIC - i am concerned that i should be testing between all conductors seperately when changing the CU and recording the results accordingly. Any advice please.
test L and N (shorted together) to E, first at 250V, then at 500V. do not test across L /N. as you rightly say, damage could be caused.
Reply to IR Testing lighting cct with fixed bathroom extractor load in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...