IR testing MICC | on ElectriciansForums

Discuss IR testing MICC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

Bradzz

Hi all
my problem is when IR testing MICC the readings keep droping to 00M ohms:sad_smile: i have 29 circuits to test in a large building, and the circuits i have so far tested have all been 00M Ohms ? could any one offer me some advice please. Bare 2L 1.5mm MICC.
[ElectriciansForums.net] IR testing MICC
Any other problems i might come accross would be most appricated:D.

Cheers people
[ElectriciansForums.net] IR testing MICC
 
When finished with the IR test earth the conductors you just tested to disapate the charge as MICC acts like a capicitor when testing
 
Hi all
my problem is when IR testing MICC the readings keep droping to 00M ohms:sad_smile: i have 29 circuits to test in a large building, and the circuits i have so far tested have all been 00M Ohms ? could any one offer me some advice please. Bare 2L 1.5mm MICC.
[ElectriciansForums.net] IR testing MICC
Any other problems i might come accross would be most appricated:D.

Cheers people
[ElectriciansForums.net] IR testing MICC

Well that's obviously not right is it, so you must have connected loads on these circuits you've tested. What's the values your getting for L-E/N-E?? Really need a lot more information, before anyone can give you guidance...


 
Hi all
At the DB i disconnect Phase Nuetral linked them together for the lighting circuits, then test to outer of MICC.
also i have tryed P-N/P-E/N-E all the same 00, My brain is hurting as i cant understand why this is happening on all circuits inc socket outlets.
some circuits show a value then just drop off to 00 the tester bleeps each cycle, the time it gets to the second beep this is about every 1 to 2 seconds is down to 00.
Light switches in both positions. i have also broken down some of the circuits and using a wonder lead checked i have the correct Phase and Nuetral.
any other infomation you may require to give me some advice jsut ask.

Thanks all for your help cheers people. and for the quick replies.
 
is the tester okay? have you pressed the button without connecting it to anything at all to see if it is faulty?
 
Tester is all good new batts put in the same day, also checked againts my check box. Will take 2 more testers with me.
re checked today all good.
 
Single phase Board and i have removed each circuit i have tested, removed the nuetral from the nuetral bar, the only thing that is common is the outer of the MICC earth connection to the DB.

all circuits show 00 ohms as in dead short, i understand that 00 Mohms could mean that the value would be lower but not a dead short, but as said the reading is 00 ohms.
 
Last edited by a moderator:
Hi all just to let you know, LOL the installation came up trumps well alomost, it tested out OK, im still scratching my head.
The only thing thats was different was No people in the building. LOL. oh well all done now, cheers all.
 

Reply to IR testing MICC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
705

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
632

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • [Speak๐Ÿ—ฃ๏ธ AA]โ„ขHow do I speak to American customer service?24&7!!Fast!!Service
    ๐“ฃ๐“ธ ๐“ฝ๐“ช๐“ต๐“ด ๐“ฝ๐“ธ ๐“ช ๐“๐“ถ๐“ฎ๐“ป๐“ฒ๐“ฌ๐“ช๐“ท ๐“๐“ฒ๐“ป๐“ต๐“ฒ๐“ท๐“ฎ๐“ผ ๐“ต๐“ฒ๐“ฟ๐“ฎ ๐—ฟ๐—ฒ๐—ฝ๐—ฟ๐—ฒ๐˜€๐—ฒ๐—ป๐˜๐—ฎ๐˜๐—ถ๐˜ƒ๐—ฒ ๐“ฒ๐“ท ๐“ช ๐“บ๐“พ๐“ฒ๐“ฌ๐“ด ๐“ฝ๐“ฒ๐“ถ๐“ฎ, ๐”‚๐“ธ๐“พ ๐“ฌ๐“ช๐“ท ๐“ฒ๐“ท๐“ฒ๐“ฝ๐“ฒ๐“ช๐“ฝ๐“ฎ ๐“ช ๐“ป๐“ฎ๐“บ๐“พ๐“ฎ๐“ผ๐“ฝ...
  • What is the refundable option on ๐”ผxpedia? Cancellation Policy ยฎ
    What is the cancellation policy for ๐”ผxpedia? ๐”ผ๐•ฉ๐•ก๐•–๐••๐•š๐•’ ๐• ๐•—๐•—๐•–๐•ฃ๐•ค ๐•’ ๐•˜๐•–๐•Ÿ๐•–๐•ฃ๐•’๐• ๐Ÿค๐Ÿฆ-๐•™๐• ๐•ฆ๐•ฃ ๐•”๐•’๐•Ÿ๐•”๐•–๐•๐•๐•’๐•ฅ๐•š๐• ๐•Ÿ...
  • [[Official~Expert]] Contact QuickBooks Desktop Support Customer Service HElp QB Support
    To contact QuickBooks Desktop Support via phone, dial โœ…๐Ÿ“ž +1-844-881-9274 +1-844-881-9274 or #...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top