Hi there, I was wondering would someone be able to give me a little advice as I'm about to do a periodic on a horrible office that has all sorts of equipment above the suspended ceilings and has those fancy thorlux fittings with the eco pots. Im a little scared of wapping 500v volts down the cables as I dont want to blow anything, its happened to me before and cost me a few pennies to fix! Anyways, Would it be fine to just do the test between L - E on all the circuits? this wouldnt do any damage would it? How do you go about testing building like this?

Cheers
 
no it wouldnt do any damage but if you join l n together and then test to earth using 250v first if you get a good reading increase to 500v the above test is method test 2 and is perfectly ok refer to gn3
 
ahh right, one more thing. How would I fill these results on a test cert? what would go in each box for Line/Neutral, Line/Earth, Neutral/Earth
Also is this method allowed for new installations? for buildings ive not wired but Im testing and am a little unsure of whats in hidden away?
 
well, you can enter your figures in the L-E and the N-E boxes, but in the L-N box enter N/V. in the comments section, note thae L-N IR tests were not done due to connected equipment.
 

Reply to IR testing question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top