I have come across an issue that i know others would have.....
I done an Insulation resistance test on a lighting circuit with no selv or pelv just regular pendants circuit. Now the customer informed me they had a leak from a bathroom a few months ago and when i tested this particular circuit my first result came out at 0.4 mega ohms at 250v (method 2).
Now i know this could be down to the water damage or something in circuit electrictronic etc so i took another 3 readings at once and the readings went up by 0.2 each time so i thought id try and see if i could get to 4 mega ohms.
After about 20 tests i could achieve over 4 on L-E and over 5 on N-E on 500v method 2.
I must be drying out any damp in the cable when doing each test but leaving for half an hour the next result went down to 2.5 and 3.0 respectively.
Now customers leak has been "fixed" by plumber but the circuit must still have an issue.
How can i make sure its all ok without ripping up the floorboards and replacing the circuit cabelling affected, could i just keep doing the test like above?
Any help much appricated.
Thanks
Matt
I have come across an issue that i know others would have.....
I done an Insulation resistance test on a lighting circuit with no selv or pelv just regular pendants circuit. Now the customer informed me they had a leak from a bathroom a few months ago and when i tested this particular circuit my first result came out at 0.4 mega ohms at 250v (method 2).
Now i know this could be down to the water damage or something in circuit electrictronic etc so i took another 3 readings at once and the readings went up by 0.2 each time so i thought id try and see if i could get to 4 mega ohms.
After about 20 tests i could achieve over 4 on L-E and over 5 on N-E on 500v method 2.
I must be drying out any damp in the cable when doing each test but leaving for half an hour the next result went down to 2.5 and 3.0 respectively.
Now customers leak has been "fixed" by plumber but the circuit must still have an issue.
How can i make sure its all ok without ripping up the floorboards and replacing the circuit cabelling affected, could i just keep doing the test like above?
Any help much appricated.