M

Mattyi26

Hi all,

I have come across an issue that i know others would have.....

I done an Insulation resistance test on a lighting circuit with no selv or pelv just regular pendants circuit. Now the customer informed me they had a leak from a bathroom a few months ago and when i tested this particular circuit my first result came out at 0.4 mega ohms at 250v (method 2).

Now i know this could be down to the water damage or something in circuit electrictronic etc so i took another 3 readings at once and the readings went up by 0.2 each time so i thought id try and see if i could get to 4 mega ohms.
After about 20 tests i could achieve over 4 on L-E and over 5 on N-E on 500v method 2.
I must be drying out any damp in the cable when doing each test but leaving for half an hour the next result went down to 2.5 and 3.0 respectively.
Now customers leak has been "fixed" by plumber but the circuit must still have an issue.
How can i make sure its all ok without ripping up the floorboards and replacing the circuit cabelling affected, could i just keep doing the test like above?
Any help much appricated.

Thanks

Matt
 
I think its kinda tricky to answer this as there are so many unknowns. But it is clear a reading such as you have will require FI. Even if that means taking up floorboards. Can you get an inspection camera in there ? The reading going up is really just your battery wasting away charging up the circuit.
 
Hi Matt, yes - what V said. If you want to start digging - I've seen some nasty cabling at top o pendants, partic if it's an older instal and someone has added a timer fan and then loose insulation and dirt (and then water...). So is there a pendant beneath the bathroom that might have been water affected? Remember to safe isolate :)
 
As handysparks says the fault is likely to be at a cable connection, because the insulation is removed at that point and water can collect.
Taking down each light fitting and ensuring you have inspected all the cable joints, remembering that it would have to be a thin film of water for this sort of result, should eliminate most of the problems, the next part would be discovering if there are junction boxes in the above ceiling space. Your inspection of the lights should have given you a clue as you would know the wiring method and the expected number of cables. If there are junction boxes then this is down to taking up floor boards.
 
With an older install,or other influences,such as water,an actual physical inspection is always a good move.

The raise in readings from a fail to a pass,does not infer confidence,as it is only a limited spread.

I have had excellent readings,far in excess of the OP's,and then a visual discovers large sections of missing insulation,on VIR,with bare conductors strung like telegraph wires...

As with all test and inspect,one set of readings or sightings,are only part of the picture.
 
With an older install,or other influences,such as water,an actual physical inspection is always a good move.

The raise in readings from a fail to a pass,does not infer confidence,as it is only a limited spread.

I have had excellent readings,far in excess of the OP's,and then a visual discovers large sections of missing insulation,on VIR,with bare conductors strung like telegraph wires...

As with all test and inspect,one set of readings or sightings,are only part of the picture.
We have no idea the age of the ops installation.
 
Hi,which is why i included an "or" in my first sentence :)

As with most of these conundrums,all missing history and information,makes it very hard to make accurate assessments.
I feel my last sentence is correct,even with NO information.

The crux of my witterings,was aimed at not assuming repeated testing was "curing" any issues,and to investigate what they could be.

I also,am very aware of the cost/time/inconvenience constraints,placed upon sparks,by the great british public...a restriction i have not,and would not endure ;)
 
Hi,which is why i included an "or" in my first sentence :)

As with most of these conundrums,all missing history and information,makes it very hard to make accurate assessments.
I feel my last sentence is correct,even with NO information.

The crux of my witterings,was aimed at not assuming repeated testing was "curing" any issues,and to investigate what they could be.

I also,am very aware of the cost/time/inconvenience constraints,placed upon sparks,by the great british public...a restriction i have not,and would not endure ;)
Am agreeing here but the op maybe chasing shadows as the IR before the leak isn't known. I would give it a few weeks then retry it.
 

Reply to IR testing result in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
759

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top