Hi All- New to this - loving the challenges!

EICR'd my house and found one of my ring finals had an IR problem- just getting to grips with testing and trying to gain experience- college was good, however, felt like it was more of learning to pass exams!

My ring final has an issue- if i test with breaker open-(off) L(load side of breaker) to E (earth bar) = good reading, N(neutral bar) to E= good reading- but L to N a bad reading. so if a possible dead short between L-N why doesn't breaker trip?

However, if i do a IR L and N to E i get a good result!

Sorry for my inexperience but can anyone help me?
 
Found one last week. Extension lighting spurred of through 5 Amp fuse from RFC. Spur behind double bed headboard upstairs.

ALWAYS do 250V test first to find loads not found on visual examination, customer memory/knowledge failure.

I've often found readings in the range of 0.04Mohms for mobile phone/door bell transformers etc... and 0.24-0.26Mohms for neon switches.
 
thanks all - found the load in loft- but also e happy with the result i had l+n to e - good to have a bit of reassurance - cheers
also lol on a funny note - or not- what can be done about a neighbours alarm going off-any veiws on the law if i rip out main fuse lmao ! providing no battery back up - ffs lol - spose just call enviromental is best option !!
 

Reply to IR Testing??? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
948

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top