Carried out an EICR on an older installation at the start of the week prior to a mains board swap over. I had a low reading on one of the ring main IR tests, between live & neutral 0.02MOhms. I couldn’t see anything plugged in or switched on anywhere on the circuit & at that point I couldn’t gain access to the attic to see if there was anything that could affecting the test as the customer was away & it was locked. The live to earth was 150m Ohms, neutral to earth 185m Ohms. I swapped the mains over today & the circuit isn’t tripping the RCBO. If it was a fault in cable would that reading cause it to trip? Customer is home start of next week so can’t gain access to attic until then.