E

electek

Hi , Im looking at doing a rewire on a small 3-bed semi. Im pretty much upon the current regs e.t.c. and am aware of the need to prevent complete loss of lighting (i.e upstairs and downstairs) in the event of an RCD tripping e.t.c

However as apparantly there is a need to protect all cabling installed less than 50mm deep in walls e.t.c. i understand both upstairs / downstairs lighting circuits must have the RCD protection.

Therefore my question is would it be acceptable in a small house to install a 30mA RCD Incomer and protect all circuits after this with MCB's rather than going to the expense of either multiple RCD's or RCBO's , after all it is only a small property and i noticed that my proffesionally wired parents two bed semi is wired this way (one 30mA RCD protecting all circuits)

Also if the property was not residential i.e a small shop how would this affect the requirements for RCD Protection

Any help much appreciated.

Cheers.
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

RCBO's to allow for discrimination. You can't have just one RCD covering all of of the circuits, your parents consumer unit was incorrectly configured.
 
Last edited by a moderator:
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

Without being rude your not clued up on the current reg's
Dual RCD , Mains Isolator lighting split between the two rcd's or complete rcbo's dedicated circuit for smokes etc etc :eek:
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

what expense ? new 17 ed boards can be got for ÂŁ80 or therabouts, Volex 10 way 17 ed boards are on special offer my way for ÂŁ59 at the mo.
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

Its not just the cost bud, Its against regs. You have to provide some sort of discrimination.

ps 10 way twin rcd Hagar board 38 quid plus ÂŁ1.50 a breaker at CEF for us. Max 53 quid all in!!
RCBO's are the ideal solution but lets face it, 90% of people just dont wanna pay for them!
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

Wylex 10 way dual split, inc breakers and change out of ÂŁ65.00 on the net delivered to your doorstep. Pre assembled so no p*****g about putting it together. Also possible to configure it to have 1st way next to main switch non RCD so you can drop a RCBO in for your smokes.............cheap as chips, fully compliant and enough left to pay for sandwiches, beer and smokes:D
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

my inprogress garage conversion is on a 30ma rcd covering lights in and out and sockets!! mind you it supplys 5 sockets 4 lights and thats it!!

plus its totally seperate from main house CU! so probably not too bad! if it trips you lose power to ONE room!
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

my inprogress garage conversion is on a 30ma rcd covering lights in and out and sockets!! mind you it supplys 5 sockets 4 lights and thats it!!

plus its totally seperate from main house CU! so probably not too bad! if it trips you lose power to ONE room!


If you read a bit futher if the installation is under the supervision of a comitent or trained person then rcds are optional, so lock your door and your still covered. hehe
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

What about if TT system. Surely you need rcd to cover whole installation?!?
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

What about if TT system. Surely you need rcd to cover whole installation?!?
Correct & you would by using either rcbo's for every circuit or by using a dual rcd cu.

As for the OP it's not a good idea to have a single rcd covering the whole property.......in fact it's a right royal pain in the backside (mine was untill i re-wired & changed the cu)
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

Is it against regs though? Reason for question is I have just done new build install where builders supplied materials including Rcd main switch consumer unit!!
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

seriously its a pretty grey area...!! the regs give you too many reasons o use a RCD i.e cables less that 50mm, competent persons, blah blah blah, but if your customer supplied the materials and said thats what they want what can you do...!!

the circuits are RCD

ok you dont hve discrimination as per the regs but what do you do!!! if that the case why do wholesalers still sell 12 way CU with one rcd..???
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

ok you dont hve discrimination as per the regs but what do you do!!! if that the case why do wholesalers still sell 12 way CU with one rcd..???

The wholesalers can sell what they want to they want it is up to the customer to decide what to install. It is because of this the cowboys get the cheepest and chuck it in. have a look at a well known DIY shop and see whet they sell to anyone without any guidelines.
 
Re: Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendati

What about if TT system. Surely you need rcd to cover whole installation?!?

You are correct, but you would install one at a greater rating than 30Ma as the incommer and individual ones of a lesser rating for your circuits.
 

Reply to Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendations in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top