Hi there,
I'm installing two ovens, each with a total load rating of 3.5kW. (see details of oven here). The kitchen already has a 20A double pole switch and a 45A dual outlet plate. Is the switch sufficient because I've calculated that the current is likely to exceed 20A? However, I'm not sure if these calculations are correct!
Calculations
This is above the 20A rating of the double pole switch. However, I'm not sure I should have included the 5A allowance for the socket outlet?
Hob
I'm also installing a hob with total load rating of 10.8kW. This would be connected to a second pre-existing 20A switch via a second dual outlet plate. Again, I've calculated that this will exceed 20A, even if I omit the 5A allowance for a socket outlet.
Calculations
Many thanks for your advice,
Katie
Calculations
- the total current of the two ovens is (3.5kW x 2 ovens)/230V = 30A
- The diversity is therefore 10A + 5A (allowance for socket outlet) + (30% of (30A - 10A)) = 21.1A
Calculations
- the total current of the two ovens is 10.8kW/230V = 47A
- The diversity is therefore 10A + 5A (allowance for socket outlet) + (30% of (47A - 10A)) = 26A
This is above the 20A rating of the double pole switch regardless of whether I include the 5A allowance for the socket outlet.
Based on the ovens and hob ratings, what would you recommend? Can I wire two ovens to one dual outlet plate which is connected to a 20A double pole switch? And can I wire the hob to the second dual outlet plat also connected to a 20A double pole switch? Or should I replace those switches with, say, a couple of 45A switches? Is there one in between 20A and 45A that I'm missing?