I have been asked to carry out intial testing and inspection of a large, new commercial project and have came across a ring main wired in twin + cpc 1.5mm cable, which serves two 2kW panel heaters. The cables are clipped direct for part of the run and for the remainder they are within an insulated Gyproc partition wall. The protective device is a 20A type B and the cable run is 20 metres. I appreciate that it is normally 2.5mm csa cable used for this purpose, however I have looked at the 17th Edition regs and it appears that the rating of a 1.5mm twin + cpc ran in insulation (worst case) is roughly 10A. I would normally replace a circuit like this just to be on the safe side but this would mean lots of associated builderswork and costs for this new client and I would like to avoid if possible.
P=IV / I/PV
> I=P/V I=4000W/230V = 17.39A
i would appreciate your feedback guys, cheers.