I have been asked to carry out intial testing and inspection of a large, new commercial project and have came across a ring main wired in twin + cpc 1.5mm cable, which serves two 2kW panel heaters. The cables are clipped direct for part of the run and for the remainder they are within an insulated Gyproc partition wall. The protective device is a 20A type B and the cable run is 20 metres. I appreciate that it is normally 2.5mm csa cable used for this purpose, however I have looked at the 17th Edition regs and it appears that the rating of a 1.5mm twin + cpc ran in insulation (worst case) is roughly 10A. I would normally replace a circuit like this just to be on the safe side but this would mean lots of associated builderswork and costs for this new client and I would like to avoid if possible.

P=IV / I/PV
> I=P/V I=4000W/230V = 17.39A

i would appreciate your feedback guys, cheers.
 
The protective device is oversized for the cable. You could downsize it to an appropriate size - most likely a 10A, which is turn isn't that likely to hold during the winter. I think you're likely to be upgrading the cable size or running in a new circuit to one of the panel heaters.
 
Would I be better off splitting the ring circuit into two radials and having two separate 10A MCBs at the distribution board? it would be easier to split the ring as the interconnecting leg between both spur's is clipped direct on the facing of the wall.

Thanks
 
I would say it's 'almost' OK!!!
Are the heaters equidistant from the supply (ie both legs carrying 9A), if so, and nothing else can be connected to the circuit, I'd pass it but make a note on the report.

Plus, specify that nothing else should be added to this circuit.
 
Last edited by a moderator:
fig.3.4 (p 249 in the red book), shows you that a 16A type B MCB requires 23Ato break in 10,000 seconds. at 17A it's off the graph, so theoretically it will never trip at 17A
 
fig.3.4 (p 249 in the red book), shows you that a 16A type B MCB requires 23Ato break in 10,000 seconds. at 17A it's off the graph, so theoretically it will never trip at 17A

The cables running in an insulated wall would put me off fitting a 16A MCB

That said it's a ring - not had any dealings with a 1.5MM, and not sure how to go about working out the CCC of the cable in that case.
 
I think it meets the requirements of the regs, albeit a bit close to the limit.:helmet:
For parallel conductors (bit dicey here) carrying equal current then you add the CCC of the cables.
Since if it is buried in insulation as the worst case then the CCC total is 20A. This is the CPD installed; but I would note the situation on the report.
 

Reply to Is a 1.5mm twin + cpc ring main ok for two 2kW panel heaters?????? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
656

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top