Have you any photos?

While I have never worked on them, I have seen terraced houses in London that were TT supplies fed from what looked like normal underground cables.
 
[ElectriciansForums.net] Is it a tt supply
 
Last edited:
The earth cable on the right of met, just dissappears into the ground with the service cable apparently.
I can't be sure, but that looks smaller than 16mm, maybe as small as 6mm? That would be consistent with it being a TT rod and not a supply TN earth.

You might find Zs is very low like TN if bonded services are large and/or linked to TN supplies in other houses, but if you can identify the conductor that is the means of earthing then a Ze test would confirm it is likely TT if somewhere in the, say 5 ohm to 200 ohm region.

Can you see if it has an incomer delay RCD, or if all boards are all RCD/RCBO?
 
I can't be sure, but that looks smaller than 16mm, maybe as small as 6mm? That would be consistent with it being a TT rod and not a supply TN earth.

You might find Zs is very low like TN if bonded services are large and/or linked to TN supplies in other houses, but if you can identify the conductor that is the means of earthing then a Ze test would confirm it is likely TT if somewhere in the, say 5 ohm to 200 ohm region.

Can you see if it has an incomer delay RCD, or if all boards are all RCD/RCBO?
I can't seem to view the pic but if it is 6.0 this doesn't mean too much.
 

Reply to Is it a tt supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
746

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
703
  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
3K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top