While local rules may apply, generally speaking the safety of a contained cable more depends on what is protecting it one end (fuse / circuit breaker) and what the load is the other end. The question is a little too vague to answer really.
 
What do you mean be 'ECC'? Initially I though that was "earth continuity conductor" (our UK equivalent is CPC for circuit protective conductor) but then you say it is at 240V which is not making sense.

Also what do you mean by "chunking" ? Was it some strange auto-correct of trunking ?
 
What do you mean be 'ECC'?
Earth Continuity Cable - I've come across this term in other countries before for just about any cable that contains a CPC, sheathed or unsheathed. I did a charity job in Zambia once and explaining what I wanted was impossible until I learned this term!
 

Reply to Is it safe or proper to run 10mm ECC cable with a voltage of 240v in chunking? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Can to OP clarify if this extension is just another room on the side of the building (so multiple cables going through the walls for lights...
Replies
6
Views
985
  • Question
Are you meaning running two 6mm cables in parallel? This is allowable in UK regs, providing the two runs are exactly the same length and routing...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top