I am replacing the wiring in a lean-to shed that has a spur directly from the house ring main. I have done quite a bit of reading on this site and produced a wiring diagram that works in the rather odd shed but is as simple as possible. I would be very grateful if someone with a bit of experience could cast their eye over it and confirm it is safe. I attach the diagram. Many thanks in advance.
 

Attachments

  • Washhouse wiring diagram.pdf
    91.3 KB · Views: 36
The basis seems fine, although I'm thinking it's a bit messy in terms of layout - you'll have a bunch of SFU's that probably don't need to be there.

If you used 4mm cable to spur off from the main house you install a cheap garage CU and just have a 16A MCB fed radial for your sockets and a standard 6A lighting circuit.
 
The basis seems fine, although I'm thinking it's a bit messy in terms of layout - you'll have a bunch of SFU's that probably don't need to be there.

If you used 4mm cable to spur off from the main house you install a cheap garage CU and just have a 16A MCB fed radial for your sockets and a standard 6A lighting circuit.
Thanks for the comments: I will check the suggestions out.
 
Thanks for the comments: I will check the suggestions out.
NB - I'm making a rash assumption here that the original house ring that will feed the spur has 30mA RCD protection already - otherwise you DEFINITELY need to look at a garage CU with an RCD.

However....... it's also just occurred to me that if you install a consumer unit, irrespective of it being fed via a spur, then it's probably notifiable work under Part P (others may correct me on that). @telectrix @Strima ??
 
NB - I'm making a rash assumption here that the original house ring that will feed the spur has 30mA RCD protection already - otherwise you DEFINITELY need to look at a garage CU with an RCD.

However....... it's also just occurred to me that if you install a consumer unit, irrespective of it being fed via a spur, then it's probably notifiable work under Part P (others may correct me on that). @telectrix @Strima ??
The house ring doesn't seem to have RCD protection, so looking more likely that I will need to add that.
 

Reply to Is my wiring diagram OK in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Ask your electrician when they do a site visit as to what is required they can also notify the installation to Building Control under Part P of...
Replies
1
Views
456
No. Chauvin Arnoux wouldnt play ball. I thought I had sussed with the capacitors but no. We've too busy with work since to really look into it.
Replies
2
Views
909

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top