Hi all,
I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior Tesla EV charger.
The Tesla charger is three phase and to be a 22kw supply at 32A.
TESLA SPEC: The wall charger itself features a built in RCD Type A + DC fault protection at 6mA. AC earth fault interruption automatically detects an AC current mismatch between power delivery conductors that would indicate current is flowing through the earth conductor. AC fault protection will trip at 20mA. DC earth fault interruption automatically detects DC leakage through earth.
After looking in the regs book (reg no 722.531.3.101) my understanding is that this would not require an RCD on the supply cable and fed via an MCB at the main house consumer unit (TN-C-S system)
I would love to know your thoughts on this as I have had advice suggesting both. I did speak with NICEIC as they implied it was a grey area much to my surprise!
Any feedback would be greatly appreciated
Ryan
I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior Tesla EV charger.
The Tesla charger is three phase and to be a 22kw supply at 32A.
TESLA SPEC: The wall charger itself features a built in RCD Type A + DC fault protection at 6mA. AC earth fault interruption automatically detects an AC current mismatch between power delivery conductors that would indicate current is flowing through the earth conductor. AC fault protection will trip at 20mA. DC earth fault interruption automatically detects DC leakage through earth.
After looking in the regs book (reg no 722.531.3.101) my understanding is that this would not require an RCD on the supply cable and fed via an MCB at the main house consumer unit (TN-C-S system)
I would love to know your thoughts on this as I have had advice suggesting both. I did speak with NICEIC as they implied it was a grey area much to my surprise!
Any feedback would be greatly appreciated