This is a SWA question.
If I have a length of SWA that is not long enough to reach a plastic CU can I jubilee clip around the armour and run an earth braid or cable to the CU.
Basically what has happened is the new CU has been dropped down to a position lower than the old one because it is larger than the old one.
The SWA cable is earthed by the armour.
The two current carrying cables inside the armour are long enough to reach the new CU but the armour is not.
So to earth the armour is it OK to tighten a jubilee clip around it and insert earth cable into the jubilee clip so once the jubilee clip is tightened up a secure connection is made.
The SWA cable is inside trunking and the connection with the jubilee clip will be insulated well with earth insulation tape after.
Is this a dodgy cowboy tactic or is this acceptable?
Cheers.