Hi all,

New to the forum! Quick background on me: I have a degree in electrical engineering and spent many years working with qualified electricians on house re-wires. I never qualified as an electrician as I went down the IT route but I can rewire a house with no concerns - not that I would as I'm not qualified!!

A friend of mine asked me to review the electrics on his new extension as he is not happy with the work. Here is what I found:

1. None of the back boxes are earthed. Not a failure but poor practice

2. Loose socket back box and broken light box (missing lug).

3. Ring main cable passing through back of lighting back box ( switch box is level with socket in kitchen).

4. Breakers labelled wrong on the new DB.

5. Live wire sticking out the wall with no termination block! I fixed this one as super dangerous.

6. Live wires sticking out the ceiling with no termination block. Also dangerous but out of reach. Not fixed.

7. Armoured cable missing gland and outer casing not earthed.

8. Light switch in bedroom not screwed in to back box. I fixed this one as dangerous.

Photos attached of some of these. The builder did the electrics and signed it all off. There are a number of issues with the extension- not just the electrics. If I was an inspector I would not have passed it! However, poor practice does not necessarily equate to a Part P failure. So my question is do any of the above actually constitute as a failure?

Thanks in advance,
Glenn
 

Attachments

  • [ElectriciansForums.net] Is this a Part P failure?
    IMG-20221226-WA0000.jpg
    552.7 KB · Views: 138
  • [ElectriciansForums.net] Is this a Part P failure?
    IMG-20221226-WA0001.jpg
    213.6 KB · Views: 119
  • [ElectriciansForums.net] Is this a Part P failure?
    IMG-20221226-WA0002.jpg
    196.4 KB · Views: 138
Following the "sign off" by the builder, has,
an Electrical Installation Certificate been issued by the builder,
and also a Building Regulations Compliance Certificate received back from the Local Authority after notification by the builder?
 
Hi all,

New to the forum! Quick background on me: I have a degree in electrical engineering and spent many years working with qualified electricians on house re-wires. I never qualified as an electrician as I went down the IT route but I can rewire a house with no concerns - not that I would as I'm not qualified!!

A friend of mine asked me to review the electrics on his new extension as he is not happy with the work. Here is what I found:

1. None of the back boxes are earthed. Not a failure but poor practice

2. Loose socket back box and broken light box (missing lug).

3. Ring main cable passing through back of lighting back box ( switch box is level with socket in kitchen).

4. Breakers labelled wrong on the new DB.

5. Live wire sticking out the wall with no termination block! I fixed this one as super dangerous.

6. Live wires sticking out the ceiling with no termination block. Also dangerous but out of reach. Not fixed.

7. Armoured cable missing gland and outer casing not earthed.

8. Light switch in bedroom not screwed in to back box. I fixed this one as dangerous.

Photos attached of some of these. The builder did the electrics and signed it all off. There are a number of issues with the extension- not just the electrics. If I was an inspector I would not have passed it! However, poor practice does not necessarily equate to a Part P failure. So my question is do any of the above actually constitute as a failure?

Thanks in advance,
Glenn
Sounds like your answering you’re own question. I’d be referring more to BS7671. Is this ‘builder’ a member of a scheme? How was the work notified? Leaving exposed live conductors!
 
Just a point, back boxes do not need to be earthed if they have a fixed lug. This is not bad practice in any way.
It's not good practice, either.

Not all light switches have an earthing ring.

I would rather fit a fly lead as there is always the chance of the back box becoming live.
 
It's not good practice, either.

Not all light switches have an earthing ring.

I would rather fit a fly lead as there is always the chance of the back box becoming live.
Absolutley nothing wrong with it. Please point me to a regulation that states otherwise.
 
Absolutley nothing wrong with it. Please point me to a regulation that states otherwise.
I didn't say it was a requirement, and I didn't say it was bad practice.
But as said, it's not good practice.
Best practice is to fit a fly lead.
Try reading GN8
 
The builder is an approved NIC EIC contractor and he has issued the certificate. I just don't understand how he can issue it with live wires sticking out the wall!

And yes the armoured cable connects to the main 100A incomer.

I'm very tempted to report him.
 
The builder is an approved NIC EIC contractor and he has issued the certificate. I just don't understand how he can issue it with live wires sticking out the wall!

And yes the armoured cable connects to the main 100A incomer.

I'm very tempted to report him.
Waste of time

Just give them a price to do the job properly
 
If the builder/sparks has issued an installation certificate that implies all is compliant with BS7671 and within timescale for building regs, there is no reason why a Part P certificate wont be issued (Did it come straight from the builder/sparks?).
A building inspector wont re-inspect the works done.
Your only recourse is to report it to NICEIC but I dont hold out much hope of them getting involved unless perhaps you can stress how dangerous the live wire situation was.
 
Your only recourse is to report it to NICEIC but I dont hold out much hope of them getting involved unless perhaps you can stress how dangerous the live wire situation was.
Take more than that. Odd unterminated live wire is fairly standard on new builds these days. Was on the one my son bought, last year.
 

Reply to Is this a Part P failure? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

I believe the 6mm and 40A MCB debate is a little contentious at times. It depends on the installation method, being pretty close to the tabulated...
Replies
3
Views
403
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top