So I understand that this is not ideal before people jump in, but I am stuck with a 2.5mm feed to the garage.

2.5mm feeding garage 27m
1.5mm in garage for lights 30m
4mm in garage feeding sockets 28m

16A mcb in house CCU feeing garage
16A mcb in garage feeding sockets
3A mcb in garage feeding lights

Volt drop to garage = 3.38%
Total volt drop for lights = 3.93%
Total volt drop for sockets = 5.52%

This seem acceptable?
[ElectriciansForums.net] Is this acceptable??
 
Last edited by a moderator:
27mtr of 2.5 in 'real world' application is a relatively short run, i rarely bother with calculating VD on such short runs.
Again at just 27mtr you should acceptable Zs as well.

What is your concern ?
 
27mtr of 2.5 in 'real world' application is a relatively short run, i rarely bother with calculating VD on such short runs.
Again at just 27mtr you should acceptable Zs as well.

What is your concern ?
When would you calculate VD?

I mean I think just that’s my idea of doing it regarding length, current carrying capacity and VD and if that’s a decent suggestion? Or if there’s a better way?
 
When would you calculate VD?

I mean I think just that’s my idea of doing it regarding length, current carrying capacity and VD and if that’s a decent suggestion? Or if there’s a better way?
Technically you should 'always' do your cable calcs , apply your correction factors and do your volt drop etc etc

But in the real world unless you are doing very long runs or high amp loads I very rarely do all the calculations ( don't tell my scam assessor that thou )
 
It doesn't comply. Your volt drop is calculated from source not individual parts of the circuit so from your calculations, I haven't done it your power circuit has a drop of 5.52% which is above 5% for a power circuit.
 
If you want to have the socket VD comply, consider either a larger cable for the socket circuit in the garage (6mm2) (or an RFC in the 4mm2).

However, if you have two B16 MCBs in series, it is going to be pot luck which one trips first on overload. It might be better to have a design e.g. with a B20 for the distribution circuit from the house, and a B16 in the garage for the sockets. Assuming of course that the cable installation method allows this.
 
I'm with SJD What about the discrimination of protective devices. If a socket trips a 16 A mcb it will more likely be the one in the Mainboard. What are you planning on load-wise in the garage.?
 
Last edited:
However, if you have two B16 MCBs in series, it is going to be pot luck which one trips first on overload. It might be better to have a design e.g. with a B20 for the distribution circuit from the house, and a B16 in the garage for the sockets. Assuming of course that the cable installation method allows this.
I completely agree with your point, but very few manufacturers state selectivity between MCBs, even Hager won't confirm that a B16 would trip before a B20.
Are we just going to ignore that thry have 2.5mm FEEDING the garage but 4.0mm feeding tht SOCKETS?
The total R1+R2 of distribution and sockets using entirely 2.5mm is about 1.2 ohms. So there (probably) isn't a need for 4.0mm for Zs purposes.
As above there's a selectivity issue between OCPDs, but that is at worst an irritation, it doesn't make it unsafe.
There's probably a "division of installation" issue regarding RCD protection too if we are talking ideals.

I assumed the use of 4mm was to attempt to reduce the reign in volt drop a little. I haven't done the maths.
Your calculations would fail from the start for breaching 433.1.1, not meeting coordination
I can't agree with you there, I can't see any reason that the sub-clauses of 433.1.1 are not met.
 
Why not just run the 2.5mm / 4mm to sockets, and use a 3A FCU off that for the lights?

It is bizarre to have a smaller sub-main than final, but I presume the sub-main is already in and hard to replace?
We're actually talking about the sockets, we haven't even started on the lighting yet! (Though these days LED lighting makes it a non issue in most cases)
 

Reply to Is this acceptable?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
456
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top